Hi Shun,
Sommer Stop is the outside temperature where the burner stops if it is above the set.
Sommer Stop Difference is the drop below
Sommer Stop which the outside temperature must do before the burner starts again.
Ex.
Sommer Stop = 18
Sommer Stop Difference = 2
Burner will stop when outside temperature is above 18
oC
...and will start again when outside temperature is below 16
oC (18-2 -
Sommer Stop -
Sommer Stop Difference).
There is no relation between
Sommer Stop and
VVB ...they can exist both without influencing each other.
Sommer Stop controls when the burner runs for heating up the house.
VVB is the function to control when the VVB (Warm Water Tank) is heated up, and if the VVB needs to be heated up while the burner is stopped because of
Sommer Stop, the burner will start anyway to heat the VVB.
Best regards
Michael
Hi all.
I’m studying the basic works by MHES now. Many thanks and respect for fundamental.
have questions.
What’s the logic of using Sommerstop and Sommer Stop difference values? Just ban on ON/OFF?
What’s the relationship between SommerStop and VVB?
Hilsen