Pillefyr => Boink, Scotte, Woody, Biocomfort, RTB => Emne startet af: rekuper efter Jan 10, 2008, 07:03
-
Hello,
could you help me, please? I have momentaly the problem probably with photosensor and there is seen on the control box screen such a message like "no fire" or "0lx" even if the bioler is running and temperature is growing up. Sorry for english, I am from czech republic.
Regards
Jiri
-
ok i wil try..
sometimes there can be some dirt on the sensor... try clean it first.... if that doesent help..... i think it is defekt...
Søren
-
Hello,
could you help me, please? I have momentaly the problem probably with photosensor and there is seen on the control box screen such a message like "no fire" or "0lx" even if the bioler is running and temperature is growing up. Sorry for english, I am from czech republic.
Regards
Jiri
Hi Jiri
You can contact www.opop.cz , they have spareparts for the burner,
You can allso call me to find out what is wrong the photo censor.
Regards Jannich
0045-96892632
-
Sometimes this photo sensor is broken because of an open circuit at the crimp between the photo sensor-element and the wire inside the photo sensor house.
Open the sensor house, check for open circuit from the sensor-element to the wire.
A solder iron will do the repair unless the fault is right at the sensor-element, then it is "new sensor".
/Hans